Surge protection on thermocouple inputs

Status
Not open for further replies.

oldfieldguy

Electrical
Sep 20, 2006
1,573
Didn't find anything definitive in a search here, and I Googled the web, too.

One of my minor stations took a pretty good lightning hit during a recent storm and blew a bunch of I/O cards, all RTD and thermocouple inputs.

Not really in my purview as a power guy, but is there a particular surge suppressor made to be inserted between the thermocouple wire going to the field and the I/O card for our control system.

I found several different surge suppressors for RTD's but I seem to be missing something that will work for the thermocouple circuits. If you have specific models in mind, I'd prefer DIN rail mounting.

old field guy
 
Replies continue below

Recommended for you

Possibly remote transmitters and a 4:20 ma system.
Easy to change I/O cards.
You may be able to ground one lead of the thermo couples.
A close hit by lightning is hard to protect against.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Bill--

You've mirrored my thoughts so far. Management (and the instrumentation guys) doesn't want to go with remote transmitters because of the complexity of the changeover.

I just had a conversation with the boss bout protection against really close/vigorous hits. I was hoping somebody knew of a DIN-mount device I could put in the control cabinet between the incoming TC lines and the I/O card. Such things are common as mud for other I/O


old field guy
 
OFG --

I've had good luck with Ditek, they're mostly into commercial-grade stuff. See what you can see at or get in touch with their tech support guys.

With just a thermocouple (low impedance, small signal), you might be able to get some relief with just a bunch or 15V MOVs across the TC terminals and to ground?

Just my thoughts...

Let us know what you decide on!

Good on ya,

Goober Dave
 
Thermo couples are such low impedance that it must be common mode voltages blowing the I/Os.
Put whatever suppressors you can find on the system. The next time you get a close in hit, say:
"Wow. It's impossible to protect against a hit that close!"
And then replace the I/Os and the surge suppressors. grin
Seriously, Goober Dave may have the best answer.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
What about an intrinsic safety barrier. Although this applies a barrier 'backwards', protecting the receiver from a fault in the field (as opposed to protecting the field device from arcing/sparking due to a fault in the safe/receiver area). Why wouldn't it work?

Of course, an I/S barrier costs almost as much as a low end temp transmitter.

 