sky2020
Electrical
- May 21, 2019
- 39
For 138 kV system, solidly grounded, we choose an arrestor with MCOV > 138/sqrt(3)*1.05 = 83 kV.
For ungrounded system, we choose an arrestor with MCOV > 138 *1.05 = 145 kV.
What about for LRG or HRG systems? Do we choose the arrestor as an ungrounded system? i.e. MCOV > 145 kV?
For ungrounded system, we choose an arrestor with MCOV > 138 *1.05 = 145 kV.
What about for LRG or HRG systems? Do we choose the arrestor as an ungrounded system? i.e. MCOV > 145 kV?