Everyone,
Surge arrester is dimensioned in studies of insulation coordination to protect equipment from surge voltage traveling waves that arrive at substation originated from strokes to strike overhead transmission lines.
Imagine a waveshape like BIL(Basic Lightning Impulse) arriving at terminal of transformer(without arrester). It will be duplicated and reflected to the system. As consequence transformer , with same insulation as BIL, will have his insulation breakdown. In the sequence will happen some kind of short circuit.
If you install surge arrester at transformer terminal , they will divide the incident wave: one wave with the surge arrester discharge voltage size goes to transformer. Other one with same size but with inverted polarity is reflected to system reducing incident wave.
We define the basic characteristics of an OZn-surge arrester: maximum continuous operating voltage MCOV, duty-cycle voltage rating, discharge current and energy capability (kJ/kV).
What about switching overvoltages?:
The switching operations concerns in EHV systems :
Line energization, line reclosing, load rejection and transformer switching at no-load.
If you have one of this problem, you should calculate the energy capability of surge arrester for discharge the energy contained in this switching surge.
We are not worry to protect the equipment;-We are worry to protect the surge arrester!
Of course , if your surge arrester absorve switching energy it will offer some protection to the equipment. But the affirmative the surge arrester protect equipment from switching overvoltages can not be compared to surge arrester protect equipment from lightning discharge!
Magoo2,
I do not remember about switching capacitor banks. I can not answer this question.
Yes ! lightning arresters and surge arresters are the same animal! They were originally called lightning arresters in North America and were later called surge arresters. They are designed to handle surge voltage travelling waves NOT lightning.
Prc,
They are talking about residual travelling waves originated from an overhead transmission line finshed by a cable connected transformer. Surge arrester are installed at both junction of cable with overhead transmission line and transformer.
Surge arrester is dimensioned based on lightning discharge but must have switching sparkover capacity to support switching overvoltage of the system.
ScottyUK
At 138kV system and bellow it is common to install arcing horn at terminal of transformer instead of surge arrester. I prefer this solution.
stevenal
“surge arresters in underground cable systems are not required"
I am not talking about this.
If all lines are underground (or enclosed), including the 10kV bus, then the installation of lightning arrester is not justified. Like ScottyUK suggests, an arcing horn is sufficient!