The precast plank provider states, in their manual, that the structural concrete topping "is usually a 3,000 psi minimum mix bonded to the top of the hollowcore plank using approved cleaning and bonding procedures." However, even when questioned over the phone, the plank provider would not provide any specifics to describe the "approved cleaning and bonding prodcedures."
Therefore, through my own research, to refine our general structural notes, i included the following:
The pre-engineered, precast hollowcore floor or roof plank shall be designed and manufactured by Spancrete or equal. Plank shall be factory prepped providing a roughened surface adequate to promote bonding of structural concrete topping. Concrete topping shall be structural concrete topping; a minimum 3,000 psi mix bonded to the top of the hollowcore plank using approved cleaning and bonding procedures to include removal of all dust, dirt, grease or any debris that would prevent bonding. Joints between plank units shall be similarly cleaned. Surface roughening and cleaning shall be adequate to provide a bond to act compositely with the precast plank to form a unified structural element. Bonding agents are not necessary. Structural concrete topping must be continuous from support to support, uninterrupted by walls, expansion joints, embedded conduits or any other obstruction.
I also read that "watering" the surface, without puddles or standing water, prior to applying topping, is recommended. However, that seems vague. does anyone have more specifics on "watering"?
Does anyone have any further specifications you would recommend?
Thank you!
Therefore, through my own research, to refine our general structural notes, i included the following:
The pre-engineered, precast hollowcore floor or roof plank shall be designed and manufactured by Spancrete or equal. Plank shall be factory prepped providing a roughened surface adequate to promote bonding of structural concrete topping. Concrete topping shall be structural concrete topping; a minimum 3,000 psi mix bonded to the top of the hollowcore plank using approved cleaning and bonding procedures to include removal of all dust, dirt, grease or any debris that would prevent bonding. Joints between plank units shall be similarly cleaned. Surface roughening and cleaning shall be adequate to provide a bond to act compositely with the precast plank to form a unified structural element. Bonding agents are not necessary. Structural concrete topping must be continuous from support to support, uninterrupted by walls, expansion joints, embedded conduits or any other obstruction.
I also read that "watering" the surface, without puddles or standing water, prior to applying topping, is recommended. However, that seems vague. does anyone have more specifics on "watering"?
Does anyone have any further specifications you would recommend?