davva
Marine/Ocean
- Sep 27, 2004
- 99
We have a 3ph induction motor (350kW, 3ph, 440V, FLC=550A, 60Hz).
When the motor is switched off, a contactor closes in the mcc to energise a step down 440/35V transformer which puts 35V across 2 of the windings (U and W phase). I think the concept is to use the motor windings themselves as a form of anti-condensation heater when the motor is off.
We are experiencing motor failures and wonder if this circuit may be the cause.
I’m want to calculate the current (and subsequently work out the heat) for this arrangement.
Should I just use the stator resistance and stator reactance from the per phase equivalent circuit diagram and then double the answer (for 2 phases) to get the impedance of the two windings? (cable impedance will be included)
Any other thoughts on this arrangement would also be welcome.