learner08
Mechanical
- Mar 27, 2006
- 15
Hi!
Need some help. I've got a heat exchanger using superheated steam (10 barG at 210 deg C) to transfer heat (I know its supposed to use saturated steam but thats the way it is sadly and not able to desuperheat for the moment!!).
My problem is the system isn't functioning. I have confirmed by components to be working fine. There is a control valve before the h/ex and a steam trap after the h/ex. There is a bypass valve before the trap and a by-pass valve after the trap. The by-pass valve after the trap is connected to the condensate return line.
The whole system used to be working (might not be fine but still working!!!) but suddenly I have a problem (not enough heat transfer). Might be due to fouling but that is not my question.
My question is while I sure my steam trap is working fine and it has enough capacity (float type and about 2 times oversized), I see an improvement when I open up the by-pass line before the trap. I cannot explain this phenomena and hope someone can help.
When I open the by-pass after the trap, I can see intermittent gushes of condensate. I do not see any live steam escaping.
Need some help. I've got a heat exchanger using superheated steam (10 barG at 210 deg C) to transfer heat (I know its supposed to use saturated steam but thats the way it is sadly and not able to desuperheat for the moment!!).
My problem is the system isn't functioning. I have confirmed by components to be working fine. There is a control valve before the h/ex and a steam trap after the h/ex. There is a bypass valve before the trap and a by-pass valve after the trap. The by-pass valve after the trap is connected to the condensate return line.
The whole system used to be working (might not be fine but still working!!!) but suddenly I have a problem (not enough heat transfer). Might be due to fouling but that is not my question.
My question is while I sure my steam trap is working fine and it has enough capacity (float type and about 2 times oversized), I see an improvement when I open up the by-pass line before the trap. I cannot explain this phenomena and hope someone can help.
When I open the by-pass after the trap, I can see intermittent gushes of condensate. I do not see any live steam escaping.