Some more comments:
1) Tank desiccant dryers are an option to be considered by the owner for sulfuric acid tank vents. They are not necessary in all circumstances, IMHO.... They require maintenance of course.... Tank overpressure or excess vacuum must be considered in the original tank specification
2) If the tank is made from carbon steel with a 0.125 to 0.25 inch corrosion allowance, dryers are of minimal benefit. If the tank is located in an arid area, there is little moisture to be removed from the atmosphere. The threat of an internal wall thinning in one specific area for a 93% carbon steel tank implies that the level of the tank rarely changes. My understanding of the OP is that he was installing a new system that would be repeatedly and frequently refilled.
3) Internal tank wall thinning, when it occurs, does not show up immediately. I would incorporate an inspection as part of a three or five year plan... IMHO, internal tank wall thinning is not as much of a threat as (CS)piping failure on the acid outlet piping.... I have worked on multiple systems where "hydrogen grooving" has caused piping failure which damaged equipment and required replacement
4) I am still a fan of the "tried and true" gooseneck vent which has been used on hundreds and hundreds of installations
5) Unlike love, Sulfuric acid Tanks and systems do not last forever. I would expect a CS tank to require replacement every 12 to 20 years. Plastic tanks may require more frequent replacement. Carbon steel piping systems will probably require replacement every 8 to 12 years
6) All of the comments I have made above only apply to systems storing and transferring
NEW OR VIRGIN SULFURIC ACID !!!.... Tanks and systems storing used or spent or "waste" sulfuric acid may pose
SIGNIFICANT FIRE OR EXPLOSION HAZARDS !!!..... There have been many accidents where "hot work" was being done nearby waste water or waste acid venting systems
A remarkable (Spent)sulfuric acid tank explosion and fire occurred in 2001 at the Motiva Enterprises Refinery
Delaware City, Delaware, July 17, 2001 -----1 Killed, 8 Injured
Also
MJCronin
Sr. Process Engineer