Substation Rock Resistivity

Status
Not open for further replies.

RSChinn

Electrical
Nov 19, 2007
38
We are empirically testing substation rock spalls for resistivity and come up with around 10,000 ohm-meters of resistivity. The IEEE80 uses a typical example of 2500 to 3000 ohm-meters for substation rock resistivity. Are we way off base? Our samples are 1-1/2" drain rock.
 
Replies continue below

Recommended for you

The resistivity values of 2000 to 3000 Ohm.m referred in your post is for crushed rocks in wet conditions.

For dry conditions, the resistivity value is much higher in the order on million (10^6) Ohm.m.

 