Got an interesting discussion topic from a fellow engineer. In short, it boils down to flexible diaphragms with subdiaphragms and their deflection. For these systems, does the subdiaphragm increase the deflection of the diaphragm (either locally by the subdiaphragm deflecting beyond the diaphragm or by altering the deflection of the diaphragm)?
By my logic it does not in idealized diaphragm design. The way I understand it the subdiaphragms are there primarily to facilitate force transfer and anchorage of the exterior wall into the diaphragm. The tension tie requirements of ASCE 7-10 section 12.11.2.2.1 and similar are there to anchor the diaphragm and ensure that a complete and continuous load path exists in the diaphragm. By exclusion, I feel that subdiaphragms are not there as a structural requirement of the diaphragm and the diaphragm will have strength and stiffness irrespective of the presence of the subdiaphragms. About the only way I can visualize subdiaphragms changing the deflection of the overall diaphragm is that the subdiaphragm essentially "point loads" the diaphragm at the continuous tie points between subdiaphragms. Thus, the diaphragm loading is no longer uniformly distributed (or nearly so) but is evenly spaced point loads.
Thus, I feel that subdiaphragms will not change the deflection of a simple, flexible diaphragm. What do you guys and gals think?
I did a fairly extensive google search and review of literature and wasn't able to find anything specific to the topic one way or another. However, I didn't delve into actual research on diaphragm deflection so perhaps my answer can be found in there.
Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
By my logic it does not in idealized diaphragm design. The way I understand it the subdiaphragms are there primarily to facilitate force transfer and anchorage of the exterior wall into the diaphragm. The tension tie requirements of ASCE 7-10 section 12.11.2.2.1 and similar are there to anchor the diaphragm and ensure that a complete and continuous load path exists in the diaphragm. By exclusion, I feel that subdiaphragms are not there as a structural requirement of the diaphragm and the diaphragm will have strength and stiffness irrespective of the presence of the subdiaphragms. About the only way I can visualize subdiaphragms changing the deflection of the overall diaphragm is that the subdiaphragm essentially "point loads" the diaphragm at the continuous tie points between subdiaphragms. Thus, the diaphragm loading is no longer uniformly distributed (or nearly so) but is evenly spaced point loads.
Thus, I feel that subdiaphragms will not change the deflection of a simple, flexible diaphragm. What do you guys and gals think?
I did a fairly extensive google search and review of literature and wasn't able to find anything specific to the topic one way or another. However, I didn't delve into actual research on diaphragm deflection so perhaps my answer can be found in there.
Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries