I agree with msquared48 and BAretired both. Based on experience a double top plate works particularly in you have plywood sheathing on the outside. However like others above I have specified triple plates before.
On the jobs I worked on sheet rock was used on both sides of the studs. On jobs that I signed, when I could not get the numbers to check, I would use triple plates or other methods to distribute the load.
Another approach that has been used is to space the studs at 16" o.c., adding one additonal stud at 2' directly under the trusses.
Regarding Conventional Framing, I am not as familair with it now, as I was in the past. However I would expect that when trusses are used Conventional Framing doesn't apply.
As pointed out by Smb4050 when CF is used you must have framing that complies with the CF provisions of the code. CF in the past, gave stud size, height and spacing for walls that supported floors and roofs framed with joists. The load on the walls was limited by the maxium spans allowed for floor and roof joists. A 2x10 spanning 16' is very different than floor trusses spaning 30'.