Cap:
If you plumb cut a rafter at a ridge board, the primary reaction at that point is a horiz. force; thus there must be an equal and opposite thrust at the walls, or ceiling jsts. must pick this up, plus a vert. reaction which is equal to half the load on the roof over that 16" wall length. If you have a real ridge beam it is assumed that it takes 1/4 of the bldg. width (load) from both sides as a vert. load in bending. And to the extent that it can deflect it will tend to produce a thrust out at the walls, but much smaller than in the former case. With a ridge beam, a top bearing rafter or one hung with rafter framing hangers the reactions imparted are primarily vertical, thus not much (no) thrust. The plywood sheathing diaphragm (a shear diaphragm) also helps reduce this thrust action, even from the ridge beam deflection, if it is well nailed and blocked and properly nailed to a good shear diaphragm at the gable ends. You can see this thrust affect on a long, low pitch, bldg. where the middle of the bldg. will have the walls leaning out a bit at the top, while they are better supported near the gable ends so there isn’t much outward movement. This wall top deflection is in direct proportion to the ridge beam deflection vs. the roof shear diaphragm stiffness (deflection). You do the trig.
When you do your calcs. remember that roof L.L’s. are given on a horiz. projection, so you should convert the roof D.L. to a horiz. projection also, then use half the bldg. width as the beam span length, and calc. the bending moment. Don’t forget any overhangs. The horiz. reaction (thrust) at the ridge board is gotten by taking moments about the center of the wall and assuming no vert. reaction is possible at a ridge board. The vert. reaction at the wall is based on half the bldg. width, plus the overhang. You can convert all the loads to perpendicular and axial loads on the longer sloped length beam, and everything should come out in the wash, assuming all your geometric (trig.) and load conversions are proper. For normally dimensioned roofs we just don’t bother with this. Think a little about this problem as the roof pitch changes: at the one extreme, zero pitch, the rafter is like a floor joist, with no thrust; at low pitches the rafter is still just a floor jst. (a beam) and the thrusts are very high; the rafter becomes a beam-column as the roof pitch increases; and finally the rafters and roof sheathing act more like studs and sheathing, or a deep beam, as the pitch approaches vertical.