I think several of you guys, JAE and/vs. almost everyone else, are kinda talking past each other. JAE is simplistically and technically correct that the sloped rafter can be resolved/reacted by two vertical reactions of wl/2. This works best if there are horiz. bearing seat cuts on the rafters at both the ridge beam and also at the top of the ext. wall pls., which is usually typical anyway. You can really visualize two vert. reactions taking care of the load transfer in this case. Even then, you have the deflection of the ridge beam which will cause a trust at the ext. wall top pls., suggested by MikeMcC and CANPRO and an opposite thrust at the ridge beam, maybe from an opposite rafter. A ridge board depends upon equal and opposite horiz. thrusts of opposing rafters and then ceiling joists to pick up this thrust at the ext. wall top pls.; or collar ties which are significantly less effective at this effort since they are generally too high and induce significant bending moments in the rafters. A vertical bearing cut on the rafter, at the ridge beam almost screams some lateral/trust loading in the rafter. You might improve this detail by using one of several different pieces of hardware (Simpson or USP/Mitek, etc.) to attach the vert. cut on the rafter to the ridge beam, but you still can’t get away from the deflection of the ridge beam and some settlement of the rafter in the nailed connection of each piece of sloped seat hardware at the ridge beam, both adding-up/summing to some thrust or outward movement of the rafter at the top pls. of the ext. wall. The best solution for minimizing this thrust is a stiff enough ridge beam to minimize deflection and then birds-mouth/horiz. seat cuts at each end of the rafters. That means that the rafters should sit on top of the ridge beam, sometimes architecturally objectionable. And, that horiz. seat cut/birds-mouth cut is not acceptable if it is too deep into the rafter. It becomes a horiz. shear/lengthwise splitting problem on the rafters. I’ve seen this horiz. thrust problem many times on long/narrow buildings. Stretch a string at the top of the ext. walls, under the rafter bearings and/or top pls. and you will see the top of the walls bowing outward at the mid-lengths of the walls. Then again, a good plywd. or osb sheathing diaphragm will minimize some of this in-plane movement (thrusting movement) of the rafters.