FL_Sem said:How do we convert a current provided by an EE into a structural load?
ASCE 113 Section 3.1.8 said:Short-circuit currents produce electromagnetic fields that cause forces on the bus conductors and potentially on the equipment. The bus conductors, insulators, and supports should be strong enough to resist these forces.
The forces imparted to the bus structure by short-circuit current depend on conductor spacing, magnitude of short-circuit fault current, type of short circuit, and degree of short-circuit asymmetry.
...
Short Circuit forces can be calculated using the equations in IEEE 605.
My experience is that the structural and EE have to work together on this. The EE is really only concerned with having large enough bus to carry the current safely and efficiently, they aren't necessarily thinking about the structural aspects. I have also never had an EE do the calcs from IEEE 605 for me, they would only ever provide the short circuit design force (and some other parameters referenced in IEEE 605 such as the X/R ration) to use for each particular substation. Often, the bus span is limited by the strength of the insulator. For subs with large fault currents possible I have had to use two (high strength) post insulators at every bus support just to get spans long enough to accommodate the bus layout. I have also had to increase bus size from 4" to 6" for the same reasons.phamENG said:I thought that was typically provided as a reaction from the EE as part of the line and bus design?