When final finish is critical for architectural work (I don't do much work with water tanks), we will try to use a performance based stripping criteria (I am an engineer for a formwork and shoring company). From the commentary to ACI371-98 Guide for the Analysis, Design, and Construction of Concrete-Pedestal Water Towers, a minimum compressive strength of 800psi (5.5 MPa) is suggested for most situations.
A prior search of ACI documents provided a minimum strength of 1000 psi for stripping/striking of vertical formed surfaces for architectural finishes.
In a recent support structure for a government project, we did not strip until 1500 psi was attained and had little if any damage due to form removal.
The added cost of using a perrformance based spec is additional cylinders and additional testing, but the ability to actually know when things should be done is certainly worth it in our eyes.