- Sep 27, 2008
- 13
Dear Sir,
Am facing a problem in MCC Motor feeder not getting stoped from LCS. It was detected that the multicore control cables coming from LCS is having stray voltage in the range of 150V-270V with some mA.The distance of LCS from substation is in the range of 1-2 KMs. This stray voltage is not allowing contactor to drop as contactor VA may be less. I had grounded all the spare cores but problem does not solved. By accident I had grounded one end of snubber circuit (capacitor only)to ground & problem is solved. Now I want to asked experts how to calculate the capacitor value wrt to distance of cables & other parameters . I request please help me by sending link or formula from which I can calculate the value of capacitors.
Please find attach scheme.
Am facing a problem in MCC Motor feeder not getting stoped from LCS. It was detected that the multicore control cables coming from LCS is having stray voltage in the range of 150V-270V with some mA.The distance of LCS from substation is in the range of 1-2 KMs. This stray voltage is not allowing contactor to drop as contactor VA may be less. I had grounded all the spare cores but problem does not solved. By accident I had grounded one end of snubber circuit (capacitor only)to ground & problem is solved. Now I want to asked experts how to calculate the capacitor value wrt to distance of cables & other parameters . I request please help me by sending link or formula from which I can calculate the value of capacitors.