Anybody want to comment?
A little history. Original transformer was installed in 2006. It failed catastrophically in 2010. The manufacturer said the cause was an external fire, although I pointed out this discoloration on that transformer's case, away from the obvious fire damage.
We replaced the failed transformer with an identical unit from the same manufacturer. A site technician called me about this obvious issue.
Facts: Neither the top oil nor winding temperatures are noticeably above normal. TCG was 0.34% Dissolved gas analysis shows that in the past two years CO went from 251 to 542 ppm and CO2 went from 1493 to 3065 ppm.
Transformer feeds a unit with an 7000 horsepower motor on a Siemens GM-150 VFD. When the motor is running, the transformer is about 80% of its 8 MVA base capacity. When the motor is not running, the load on this transformer is negligible.
The standard battery of tests (power factor, turns ratio, winding resistance, etc.) were normal a year ago.
I think I'm looking at an incipient failure. I'd like other opinions.
old field guy
A little history. Original transformer was installed in 2006. It failed catastrophically in 2010. The manufacturer said the cause was an external fire, although I pointed out this discoloration on that transformer's case, away from the obvious fire damage.
We replaced the failed transformer with an identical unit from the same manufacturer. A site technician called me about this obvious issue.
Facts: Neither the top oil nor winding temperatures are noticeably above normal. TCG was 0.34% Dissolved gas analysis shows that in the past two years CO went from 251 to 542 ppm and CO2 went from 1493 to 3065 ppm.
Transformer feeds a unit with an 7000 horsepower motor on a Siemens GM-150 VFD. When the motor is running, the transformer is about 80% of its 8 MVA base capacity. When the motor is not running, the load on this transformer is negligible.
The standard battery of tests (power factor, turns ratio, winding resistance, etc.) were normal a year ago.
I think I'm looking at an incipient failure. I'd like other opinions.
old field guy