We are installing a 16" pipeline strainer ahead of a pressure control valve to keep out the bits that may plug the control valve or valve port. Do I need to install a PSV on the strainer? Are pipeline strainers considered pressure vessels?
I've seen chains and locks used or simple plastic tie wraps. In a similar thing, our pipelines has ASME pig traps. we removed the psv (mainly because the psv must be tested 2 times per year by law and the pig trap was in town). I had a sign made up that read something like this. "This piece of equipment requires a thermal relief path and the valves that must remain open are identified with a red color code. To close this valve a permit must be obtained and an alternate path for thermal rlief must be provided."
maddocks, I recently had the same problem, and it took me a while to convince the regulators that a PSV is not required.
Seem to recall the key points are:
- Design strainer for pump shut off.
- Only relief case must be fire case.
- Use ASME 8 App M to justify a PSV is not required.