NY might change things, but that's a pretty good slope and is likely to shed pretty well. That said, unbalanced loads might get interesting.
Collar ties could be straps over the sheathing which is not yet in place, so not too concerned there. And those braces are just as likely to be props used by the framers to keep things stable until everything is in place and fastened.
Prescriptively, SP No2 2x12 can still go 14' with a ground snow load of 70psf. So this still seems quite plausible as those are easily 2x10 or 2x12 in most places on the roof. Higher grade lumber or a lower snow area and it works. The valleys are certainly suspect, but good luck convincing the framer of that.