I guess there are a few issues we can all agree on:
1) Tolerable Step Potential is always higher than tolerable Touch potential (actually the Canadian Electical code has it pegged around 3 times higher for Crushed rock cover).
2)
Touch Potential is the Difference between the GPR (or the "Grid Voltage") and a place on surface anywhere near a metallic struture (actually the code refers to the normal horizontal reach considered to be 1 m)
3)
Step potential is the difference between two points on the surface separated by a distance of one pace (assumed to be 1 m).
I also have to agree with the simple equation given by
jghrist to derive the Step Potential as a difference of two Touch potentials (assuming they are apart <= 1 m).
Furthermore, if we look at a graphical representation:
The following is an actual simulation of a ground grid (it's not symmetrical as you might notice)
NOW, the Red peaks in the Absolute potential graph (corresponding to actual ground rods) represent the points on the surface that reach almost full GPR: 4600V.
The "valleys" correspond to space between the interconnecting grid elements.
The worst case Touch potential would seem to be, when someone stands in the "valley" and touches something that has full GPR (i.e. 4600V). - That is clearly shown in the second picture.
The worst case Step potential would be, when someone walks across the steepest gradient on the grid.
The thing is, I can not fathom how this gradient difference could ever be more tham the differnce between the deepest "valley" to the highest peak (GPR)??
This differnce is in fact the wost case Touch potential.
I really don't understand
stevenals statement that "Worst case Estep can easily exceed worst case Etouch."
I guess the answer may lay somwhere in the equation:
Es= (r.Ig.Ks.Kf)/(0.75.Lc+0.85.Lr) [IEEE Std D.12] that
cuky2000 has shown.
Possibly with the non-uniform current distributon in the grid elements or ground rods.
ROMANKO