I have a job which will have very steep (8.75:12) roof framed out with steel joists. I am working on the detail and would appreciate it if you all would review the attached details and provide your input/recommendations.
My primary concerns consist of:
[ul]
[li]Diaphragm shear transfer at the perimeter of the roof (detail 3). [/li]
[/ul]
[ul]
[li]Diaphragm shear transfer at the ridge (detail 4). My intent is to make the deck behave monolithically. [/li]
[/ul]
[ul]
[li]Bearing seat details, I am utilizing Bent PL3/8" for bearing seats, is this conventional construction at this depth?. Also, I have seen in other consultants details that they don't design the bearing seat but appear to leave it up to the joist engineer. Is this standard practice? [/li]
[/ul]
[ul]
[li]I have added a PL1/8 on top of the HSS collector to match the slope of the deck. Is there a better way to ensure a positive shear transfer from the deck into the collector? [/li]
[/ul]
My primary concerns consist of:
[ul]
[li]Diaphragm shear transfer at the perimeter of the roof (detail 3). [/li]
[/ul]
[ul]
[li]Diaphragm shear transfer at the ridge (detail 4). My intent is to make the deck behave monolithically. [/li]
[/ul]
[ul]
[li]Bearing seat details, I am utilizing Bent PL3/8" for bearing seats, is this conventional construction at this depth?. Also, I have seen in other consultants details that they don't design the bearing seat but appear to leave it up to the joist engineer. Is this standard practice? [/li]
[/ul]
[ul]
[li]I have added a PL1/8 on top of the HSS collector to match the slope of the deck. Is there a better way to ensure a positive shear transfer from the deck into the collector? [/li]
[/ul]