The first question is do you intend to use the steel shell to carry any of the load. If you do, you should be concerned about corrosion. At .08mm/yr, the shell would be reduced to .25 inches of shell thickness in approx. 40 years, which may be the limit of the design life. However if you figure just the concrete, the 75 tons applies 2000 psi stress to the concrete. (P/Ag). Note that a load test to 2x Design will impose a higher stress, although the shell could participate, so that the load in the concrete would be less than 4000 psi.
The next consideration is the pile driving. Driving pipes closed end is not a problem, however I have not driven pipes less than 12" There is not a big difference between driving open or closed pipes. Usually the pipe will plug tightly and act as a closed end. If you plan to fill the piles, the really should be closed end as you will never do a good job of cleaning out the pipe prior to placing the concrete. Often a flat plate is welded to the bottom of the pile, although conical points are available. I would strongly recomend a WEAP analysis in the design phase for your project due the unusual soil conditions in your project. I would use a Vulcan 01 air hammer with an aluminum mcarta cushion and see what the driving stresses and final blow count look like.
Which segways into my third consideration, the soil/rock profile. The soft soil deposits may not sufficantly brace the piles. To have a rod sink 2 feet in one blow is pretty soft. Also since the soil is so soft pile alignment will be a problem. You should expect significant out of location on these piles. Also these piles may not have good lateral stability. If that is an issue, you may want to consider batter piles. The limestone can have soft zones underlying competent rock. If this is the case, then you could have serious questions abut the bearing capacity of the rock.
Depending on the field conditions, you could get 10 inch piles to work, although I would consider 12 to lower the stress. I would not figure the cpacity of the shell into the capacity of the pile. I would be concerned about lateral support and unbraced length. I would also be concerned about pile alignment and driving stresses. I would also closely look at the bearing capacity of the limestone. As a final thought, I would consider 10 inch drilled in mini-piles that were socketed at least 5 feet into the rock. This could solve a lot of problems, including the alignment, the bearing and the driving stresses. A conversation with a local pile driver and a local mini pile installer could give you a wealth of information.
Good luck and let us know how you make out!