Can anyone see an advantage / disadvantage to putting a bypass valve/pipework around a parellel slide valve on a HP steam system 110 bar and IP steam system 30 bar
 
Replies continue below

Recommended for you

cooper24,

Can you describe your system in more detail? With more information, perhaps some useful advice could be provided.
 
The arrangement described is typical; used to
slowly introduce steam and heat up pipework
after maintenance. Much much safer than trying
to crack open a full bore 110 Bar valve. Is that
the question?
 
Yes, as "jherbert" has said, bypass of a main, HP or IP valve for warm-up is common.

You should take precautions that if the piping in question is for supply to a steam turbine (for example) that there are appropriate "permissives" in the operating system to detect open valves, and ensure against a potential hazardous condition of uncontrolled steam supply in a shut-down situation.

 
cooper,

The small bypass line is typically installed on steam piping valves for a variety of reasons:

- Allows equalization of pressure before admission of flow
(a major advantage with large, hand-operated valves)

- Permits slow heat-up of piping, minimizing condensate slugs

- Lengthens life of large-valve sealing surfaces

The need for bypass valves on large valves is discussed in a chapter on steam piping in the "Piping Handbook" by Nayyar

My opinion only...