We have a boiler generating steam to users (heat exchangers). Our steam system design if as follows:
1) Two PSVs on boiler steam drum set at 109 barg and 110 barg, respectively. PSVs are designed to ASME boiler code. PSVs are sized for 80% of maximum steam generation capacity of boiler.
2) One PSV downstream of boiler superheater at 100 barg. PSV is designed to ASME boiler code. PSV is sized for 20% of maximum steam generation capacity of boiler.
3) Steam users have an MAWP of 100 barg and are designed to ASME Section VIII div. 1. There are no PSVs located near the users. Overpressure protection for the steam users is provided only by the PSVs in the boiler package (PSV's in item 1 and 2 above).
During blocked outlet relief scenario, the PSVs in the boiler package limit the maximum overpressure to less than 116% of MAWP of the steam users (in accordance with ASME Section VIII div. 1 for multiple relief valves). However, the problem we have is that the PSVs on the boiler steam drum have a set pressure higher than 105% of MAWP of steam users (designed to ASME Section VIII div. 1). ASME Section VIII div. 1 does not allow the set pressure to be higher than 105% of the MAWP when multiple PSVs are used for protection.
The question is if the current design is acceptable based on ASME Section VIII div. 1 requirements? My opinion is that the current design does not meet all the ASME Section VIII div. 1 requirements and hence is unacceptable, but wonder if anyone has a different opinion which can be supported by code.
1) Two PSVs on boiler steam drum set at 109 barg and 110 barg, respectively. PSVs are designed to ASME boiler code. PSVs are sized for 80% of maximum steam generation capacity of boiler.
2) One PSV downstream of boiler superheater at 100 barg. PSV is designed to ASME boiler code. PSV is sized for 20% of maximum steam generation capacity of boiler.
3) Steam users have an MAWP of 100 barg and are designed to ASME Section VIII div. 1. There are no PSVs located near the users. Overpressure protection for the steam users is provided only by the PSVs in the boiler package (PSV's in item 1 and 2 above).
During blocked outlet relief scenario, the PSVs in the boiler package limit the maximum overpressure to less than 116% of MAWP of the steam users (in accordance with ASME Section VIII div. 1 for multiple relief valves). However, the problem we have is that the PSVs on the boiler steam drum have a set pressure higher than 105% of MAWP of steam users (designed to ASME Section VIII div. 1). ASME Section VIII div. 1 does not allow the set pressure to be higher than 105% of the MAWP when multiple PSVs are used for protection.
The question is if the current design is acceptable based on ASME Section VIII div. 1 requirements? My opinion is that the current design does not meet all the ASME Section VIII div. 1 requirements and hence is unacceptable, but wonder if anyone has a different opinion which can be supported by code.