We are doing de-rating of a steam generator from current 1700 psig design pressure on steam side to 1300 psig due to the lower wall thickness found in the economiser and steam generator tubes during the insepction. This is very old plant and no documentation available on original design. Please refer to the sketch attached. The set up is like this.. BFW pump with PSV on discharge side set at 2000 psig without any control valve, BFW is being preheated in the economiser and steam generated. Two PSVs are set at 1700 psig & 1649 psig respectively to meet the total relief load.
My question is if I derate the design pressure on steam side i.e. from 1700 psig to 1300 psig, do I need to reduce the set pressure of the BFW PSV as well or not?
My understanding is that since there is no control on BFW pump discharge side, the BFW PSV is protecting pump discharge piping up to Economiser inlet side of for blocked outlet(there is a block valve at Economiser inlet). And the Steam PSVs are protecting the Economiser and the Steam Generator with relief capacity equal to max. steam generator's capacity based on the heat transfer area of Economiser and Steam Generator tubes. But then why BFW PSV set 300 psig higher than the steam PSVs?
Would anyone please advise me, Thanks a lot.
We are doing de-rating of a steam generator from current 1700 psig design pressure on steam side to 1300 psig due to the lower wall thickness found in the economiser and steam generator tubes during the insepction. This is very old plant and no documentation available on original design. Please refer to the sketch attached. The set up is like this.. BFW pump with PSV on discharge side set at 2000 psig without any control valve, BFW is being preheated in the economiser and steam generated. Two PSVs are set at 1700 psig & 1649 psig respectively to meet the total relief load.
My question is if I derate the design pressure on steam side i.e. from 1700 psig to 1300 psig, do I need to reduce the set pressure of the BFW PSV as well or not?
My understanding is that since there is no control on BFW pump discharge side, the BFW PSV is protecting pump discharge piping up to Economiser inlet side of for blocked outlet(there is a block valve at Economiser inlet). And the Steam PSVs are protecting the Economiser and the Steam Generator with relief capacity equal to max. steam generator's capacity based on the heat transfer area of Economiser and Steam Generator tubes. But then why BFW PSV set 300 psig higher than the steam PSVs?
Would anyone please advise me, Thanks a lot.