Looking for anyone with experience in DP steam flow measurement with impulse lines (wet legs) 30-40 ft. in length. Having issues with the steam flow tracking the condensate flow. We're looking at a possible imbalance in the liquid legs that isolate the DP transmitter from live steam. When the legs are filled and the transmitter is zeroed at start-up, the steam measurement is reliable. After a certain period of time, the steam measurement tails off (appears to read low) and doesn't track the condensate output in a closed loop system. The DP transmitter is mounted below the primary DP flow sensor and the tubing (1/2" SS) slopes continously downward. I believe that the vent valves of the DP transmitter are oriented correctly to avoid trapped air in the diaphragm. In addition, we have found no evidence of a leak path across the equalizer valve in the manifold.
Additional Notes: Pipe Size: 30". Pipe run: Horizontal. Steam Pressure: 100 PSI. Steam Temp: Slightly above Saturation. Reading low DP's during turbine test phase(understanding that there will be an error induced at the liquid/vapor interface in wet legs due to a dynamic equalibrium). Condensate (reference) Meter: Mag
We have three other sensors in service with no problems, the only difference being that the liquid legs are only 4-5 feet in length. For what it's worth, we're measuring geothermal steam (probably not related). Has anyone experienced issues with running liquid legs 30-40 feet or more using a DP flow meter on steam? We are not concerned with absolute accuracy at start up. The problem is that the steam meter tracks the condensate meter, then falls off dramatically. Any help or advice would be greatly appreciated.