Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Static Pressure

Status
Not open for further replies.

patibar

Chemical
Joined
Sep 30, 2012
Messages
26
Location
KW
I would request somebody to help me in understanding the concept of using static pressure in Fans and blowers performance curves. Normally for centrifugal pumps there will be a characteristic curve of differential head vs Flow. Why we use statis pressure rather than the total pressure for blowers?
Where Total Pressure = Static Pressure + Velocity Pressure.

Thanks
 
It is easier, less intrusive, and less expensive to measure static pressure; no need to measure the velocity/velocity pressure. Also, if the inlet and outlet diameter of the fan or blower is about the same, there really is no need to measure velocity pressure; it cancels out when calculating the required head.

Good luck,
Latexman
 
As Latexman explained:

Fan curves are given in terms of total pressure vs.volumetric flow rate.
Total pressure loss = static pressure loss + dynamic pressure loss:

ΔPtotal = (Pin,static − Pout,static) + ½ ρ (Vin2 − Vout2)

If exit and inlet area of a duct are about the same the dynamic pressure loss (or gain) may by small and disregarded.
 