Measure the pressure at the supply side (SP Outlet)of air handler, and at the return side of the air handler (TP Inlet).
The supply should yeild a positive value, and the return a negative value.
The tatal static pressure of the air handler will SP Outlet - (minus) the TP Inlet.
i.e Pressure SP Outlet 69 Pa
Pressure TP Inlet -272 Pa
Unit Static Pressure = 341 Pa
This can also be done at the fan to give the fan static pressure