With respect, I disagree with JJPellin. A "spill back" or recirculation line helps to avoid the pump running at low flows or no flow due to valve closure or rise in downstream pressure higher than the pump discharge pressure. It does not normally do anything with regard to end of curve or run out. If the downstream pressure is low and hence flow through the pump exceeds its minimum flow, the bypass line should then close and hence flow through the pump is dependant on the downstream pressure. If you look at the other post from the OP, he has quite as strange piping layout where the re-circ line is downstream [sic] of the pump isolation valve.
timebone. You say that the pump VFD gets a start point of 100%. Do you know this or is this a guess? There may be either a specific start-up sequence where pump speed is slowly ramped up until it reaches the required set point or there could be a feedback loop whereby the speed is limited by the amps going into the motor or maybe a flow input as an overide. I believe you are correct and that the bypass loop does absolutely nothing for you in protecting the pump on start-up from high flow and if the bypass line starts open (you don't say what type it is or how it is controlled) then would make things worse not better (compressors are different and they need to start with a bypass open, but we're talking liquid pumps here).
How do you avoid "run out" when starting? - Control the speed of the motor to limit flow / power / amps to the max of the pump. Control the flow with a control valve to do the same thing. If you slow down opening of the discharge valve (you don't say if it is actuated or not)- in fact you've not given any information on size, flow, fluid, power, motor size - then this could have a similar effect.
It all depends on how big your downstream system is, how long it takes to stabilise flow, what other control functions are in the VFD, how big your system is, how much spare the motor has for running at end of curve conditions etc etc.
oh by the way, discharge pressure is pump head - just expressed as pressure instead of metres or feet
The pump curve would help you to se eif in fact your pump was going off the end of the curve or not. For that you would need to record pressure as a minimum and flow if possible during the start-up mode. It would also tell us what sort of size we're talking about here. A 25kW motor / pump is less likely to have serious issues compared to a 500kW unit.
Bottom line is that from the low amount of info you've provided, your re-circ line is in a strange place and you don't seem to have any control over flow in the event that on start-up or during operation your downstream line has low pressure compared to "normal" operation.
How about you give a better description of what this operation is, how it works, what the pressures and sizes are, what your current issues / problems are.... Then we might get somewhere
My motto: Learn something new every day
Also: There's usually a good reason why everyone does it that way