Mr. Bedoya:
The Brushless Synchronous Motor Control is not for beginners!
Here are a few pointers, though:
In order to properly size the field discharge resistor (FDR) you need to know the induced field current from the motor manufacturer. This value used to be given at 100%, 50%, 25%, and 5% slip. As the name says, this is the current induced in the field during start. You can think of the field as a current source, and never, NEVER, ever, open this circuit when the motor is running (even if the motor itself has an internal spark gap). If you don't have that value, it's best to account for both the voltage in the field circuit and, believe it or not, the inertia of the driven train (wk**2 of the shaft, the coupling, and the load). The higher the value of the FDR, the more torque the motor delivers. If the train design is correct, the delta contribution from the FDR should only affect starting time, not the ability to accelerate. On the other hand, a lower FDR value limits the voltage in the field circuit to acceptable insulation withstand levels. Through experience, you'll find that it's best to stay around 2P.U. of the field resistance. And, in agreement with a post above, keeping the voltage low is best for older equipment.
On to the controls: if you're not familiar with this, I suggest that you download from GE the uSPM (Micro SPM) instructions book, print it, and read it over and over and pay attention to the electrical schematics, and pay extra attention to the Field Application contactor make before break design, and the required surge suppression using either selenium (sp?) type rectifiers, or high Joule, 1000V MOV's.
Good Luck!