Hi Waross,
I searched this forum on this topic and found your response which is restated below, thread link is
Could you provide me with an example of "rigorous" method and the arithmetic method? Electricpete had done some calculations on that old thread, but I couldn't understand it.
Below is your response from the old thread;
"The current of the running motors may be about 80% PF.
The current of the starting motor may be about 20% PF.
The total current will be much less than the sum of the running and starting currents.
Voltage drop calculations based on the arithmetic sum of the currents will be quite conservative.
The available short circuit current as determined by the impedance of the transformer is valid only for bolted fault conditions. For a rigorous calculation of voltage drop under motor starting conditions, consideration must be given to the phase angle of the current and the X:R ratio of the transformer. Again calculations based on impedance alone may be quite conservative.
Pete, how about crunching some numbers for an example:
Take 6 equal motors running loaded at 80% PF.
Take a similar motor starting at 600% current at 20% PF.
Assume a transformer equal to the KVA load of 10 motors.
Give the transformer an impedance of 6% and an X:R ratio of 6:1
What will be the voltage drop using the simple sum of the currents without regards to phase angles and the PU impedance.
What will be the actual voltage drop considering phase angles and the X:R ratio.
If you take up the challenge I will bribe you with an lps. grin"