What is the basis for selection of star/delta winding for motors ? If we chage the connection of an existing star motor to delta or vice versa , what will be the impact ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
If a six lead motor rated 240/415 volts is connected delta at 415 volts, the iron will saturate and no amount of "cooling options" will be adequate to remove the excess heat before the motor fails due to burn out.A six lead motor can be connected in either way, subject to aqueuate cooling options done by the manufacturer
Not necessarily true. Many VFDs struggle to produce full torque at zero shaft speed due to insufficient flux in the iron.A variable speed drive would allow you to develop full torque from standstill