Hi guys,
While I was reading some other post one thing come on my mind.
There is induction motor connected for star delta start with classic scheme (three contactors: main, star and delta).
Firstly main contactor and star contactor close their contacts. Motor is accelerating and after some time star contactor open its contacts.
Then, before delta contactor close its contacts, as it is well known rotor current will continue to flow decreasing exponentialy down to zero.
Decreasing will depend on rotor time constant L/R.
This rotor current will induct some voltage on stator windings with frequency of rotor speed.
So this is the point:
In this situation motor terminals U1,V1,W1 will be on network potentials (because main contactor remain closed). On stator windings you will have in first moments voltage that is near to nominal motor voltage and this voltage will lagging in relation to network voltage. So in some next few moments (when angle between network and stator voltage reach 180 degrees) you will have approximatly double nominal voltage on motor terminals U2,V2,W2 (depending on rotor R/L and actual rotor slip).
This can be problem for motor, cable and contactors isolation.
I am interesting is this problem is well known in literature. Are there problems with isolation more often then usually on star delta starters.
Is this a thing that you must be careful or nobody care for this.
Milovan Milosevic
While I was reading some other post one thing come on my mind.
There is induction motor connected for star delta start with classic scheme (three contactors: main, star and delta).
Firstly main contactor and star contactor close their contacts. Motor is accelerating and after some time star contactor open its contacts.
Then, before delta contactor close its contacts, as it is well known rotor current will continue to flow decreasing exponentialy down to zero.
Decreasing will depend on rotor time constant L/R.
This rotor current will induct some voltage on stator windings with frequency of rotor speed.
So this is the point:
In this situation motor terminals U1,V1,W1 will be on network potentials (because main contactor remain closed). On stator windings you will have in first moments voltage that is near to nominal motor voltage and this voltage will lagging in relation to network voltage. So in some next few moments (when angle between network and stator voltage reach 180 degrees) you will have approximatly double nominal voltage on motor terminals U2,V2,W2 (depending on rotor R/L and actual rotor slip).
This can be problem for motor, cable and contactors isolation.
I am interesting is this problem is well known in literature. Are there problems with isolation more often then usually on star delta starters.
Is this a thing that you must be careful or nobody care for this.
Milovan Milosevic