Pocko
Electrical
- Mar 5, 2003
- 8
Hello all,
I'm after some opinions on the following logged readings i get when "tonging" the current drawn by an induction motor on start up. The motor is directly coupled to a centrifugal fan mounted inside the duct work of a dust extraction system.
The motor's plate rating is 72.2 A FLC. 3 phase 415 vac, 50 Hz.
The starting method utilised is Star/Delta and currently the time delay relay is set at 0.5 seconds.
As the capture method can't log in milliseconds i can't show the inrush current.
The following is data i've captured from a start up (from the red phase only) -
Log # Start Time High Units
1 10:03:36 0 A AC
2 10:03:37 0 A AC
3 10:03:38 0 A AC
4 10:03:39 115 A AC
5 10:03:40 127 A AC
6 10:03:40 128 A AC
7 10:03:41 126 A AC
8 10:03:42 124 A AC
9 10:03:43 353 A AC
10 10:03:43 384 A AC
11 10:03:44 356 A AC
12 10:03:45 130 A AC
13 10:03:45 121 A AC
14 10:03:45 66 A AC
15 10:03:46 50 A AC
16 10:03:47 49 A AC
17 10:03:48 50 A AC
18 10:03:49 50 A AC
19 10:03:50 50 A AC
20 10:03:51 50 A AC
As the voltage during the Star connected period should be 33.33% of the Delta voltage, I was expecting to attain a figure of 33.33% of the run current during the Star period of the start up, or in this case 16.66A and not in the 100's as the log shows! The figure in the 300's 5 seconds in to the start up is another concern!
As a side note in the current state if we were to set the overload using the 58% FLA rule for star/delta starting we would be in trouble, as this figure (41.76 A) would come in under our "normal" operating current and hence trip on overload.
Also as I have no access to the motor curve or the fan's inertia curve. Without this info could/should i determine the correct time for the change over from Star to Delta?
Is it possible this motors Star/Delta wiring has been hooked up to the wrong contactors?
Thanks for your time and if further info is required let me know and i'll do my best to provide it.
Cheers - Chris.
I'm after some opinions on the following logged readings i get when "tonging" the current drawn by an induction motor on start up. The motor is directly coupled to a centrifugal fan mounted inside the duct work of a dust extraction system.
The motor's plate rating is 72.2 A FLC. 3 phase 415 vac, 50 Hz.
The starting method utilised is Star/Delta and currently the time delay relay is set at 0.5 seconds.
As the capture method can't log in milliseconds i can't show the inrush current.
The following is data i've captured from a start up (from the red phase only) -
Log # Start Time High Units
1 10:03:36 0 A AC
2 10:03:37 0 A AC
3 10:03:38 0 A AC
4 10:03:39 115 A AC
5 10:03:40 127 A AC
6 10:03:40 128 A AC
7 10:03:41 126 A AC
8 10:03:42 124 A AC
9 10:03:43 353 A AC
10 10:03:43 384 A AC
11 10:03:44 356 A AC
12 10:03:45 130 A AC
13 10:03:45 121 A AC
14 10:03:45 66 A AC
15 10:03:46 50 A AC
16 10:03:47 49 A AC
17 10:03:48 50 A AC
18 10:03:49 50 A AC
19 10:03:50 50 A AC
20 10:03:51 50 A AC
As the voltage during the Star connected period should be 33.33% of the Delta voltage, I was expecting to attain a figure of 33.33% of the run current during the Star period of the start up, or in this case 16.66A and not in the 100's as the log shows! The figure in the 300's 5 seconds in to the start up is another concern!
As a side note in the current state if we were to set the overload using the 58% FLA rule for star/delta starting we would be in trouble, as this figure (41.76 A) would come in under our "normal" operating current and hence trip on overload.
Also as I have no access to the motor curve or the fan's inertia curve. Without this info could/should i determine the correct time for the change over from Star to Delta?
Is it possible this motors Star/Delta wiring has been hooked up to the wrong contactors?
Thanks for your time and if further info is required let me know and i'll do my best to provide it.
Cheers - Chris.