I just came across some information that could have a connection with your custumer's problem regarding Y/D motors.He was loosing motor windings nearly every 3 months or so.A very hi rate of winding failures.
As a rule ,we set motor overloads as per Table 44 on the CECode or possibly any code .This rule says that for motors with a Sfactor of 1.15 OLoad is set at 115% of motor nameplate FLAmps or Table 44 and 125% for motors with a 1.25 Sf.This is true for most motors unless ,they have a Star/Delta starter.
The following example indicates how to determine the OLoad setting of 75 HP ,575 volts,3phase(SCIM) controlled with a Wye/Delta starter.The motor is rated for continuous Duty and has a Sfactor of 1.2.
Sorry about the Table info.Is in the CECode.Maybe not much different in the USA or VDE rules in Europe.
Step1= Use Table 44 to determine the FLA of the motor. Table 44?--75 hp,575 v,3Ph SCIM draws 77 Amps.
Step 2==Determine the Phase value of the current.
77Amps/Sroot3(1.73)=44.45 Amps
Step 3==Use rule 28-306(1)to determine the overload setting.44.45x1.25=55.56 Amps
Step 4 == Rule says to comply with the marking requirements outlined in Ru28-306 (2)
If I wasn't thinking about a Star/Delta motor and I set my
OLoads at FLA of 77x 1.25 =96.25 Amps.it would not be hard to burn the motor out,if one wasn't paying attention.
I will be honest and admit that until today, I had never thought about it.The reason might have been,because I didn't have a problem of this nature with a Star/Delta motor.
If you have a problem,it might be worthwhile to look at the OLoad setings.
Just to make my day,tomorrow I will find out that everybody else knew about this little rule.I hope that
there is at least one person that has never heard about it.
Thank you all
GusD