Star-Broken Delta PT rating 2

Status
Not open for further replies.

keyrose

Electrical
Joined
Mar 13, 2009
Messages
4
Location
CA
I have circuit of Primary Star secondary broken delta connection connected to 12kv system.

Each individual PT ratios are 14400/120

As in star, each PTs are sublected to phase voltage only. Can I select the PT of ratios (14400/1.732)/120 for this connection?


Keyrose
 
Keyrose-

Yes. If the star point it grounded, you can use single-bushing PTs. If the star point is not grounded, you need to use 2-bushing PTs.
 
I don't understand the question. You say that VT ratio is 14400/120 (120:1) then ask if you can select it as(14400/1.732)/120. If the system voltage is 12.47 kV, then you can use 7200/120 (60:1) VTs.
 
Me too, can't follow. You already have the ratio 120:1. What's there to "select"?
 
Google search "broken delta" on this site. This has been discussed quite a bit.
Almost 400 hits.
One of the first hits.
3V0 (broken delta) Resistor Sizing
thread238-225126


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
NO, no, no. If you are applying these VTs (PTs) to a system that is not solidly grounded - which is often why the broken delta would be used - you need VTs that are rated for at least line-line on the primary. So your 14400 primary would work but your 8314 primary would be subjected to overvoltages and saturation during a ground fault, just when you need accurate response.
 
David-

Your comments are correct. However, depending on the protection, a 2-bushing PT with a L-G ratio (i.e. 7200:120) can be used if the protection will clear in a time that meets the over-voltage limits set-out in the standard (i.e. IEEEC57.13), i.e. 1.73 - 1 minute.
 
scottf,
Yes, if the protection scheme is set to clear under 1 minute on SLG faults. Some ungrounded system protection setup do not trip but just "indicate" the occurrence of a SLG fault, allowing the crew to correct the problem. It may take hours of checking and CTs can saturate.
 
scottf,

The rule does appear to be universal. Depends on indoor versus outdoor, group and on voltage rating. 140% is the 1 minute rating for many of them.
 
Stevenal-

Yes...the overvoltage factor varies with group no., that's why I listed "i.e.".
 