CuriousElectron said:
Has anyone had a chance to witness an undersized generator unable to bring connected motor up to speed?
Actually, yes.
Years ago I was in a Central American country, doing some volunteer work and just hangin out when the country was beset by a power crisis.
The entire National Grid was on 50% rationing, 6 hours on, 6 hours off.
I Found myself installing standby generators as fast as I could.
I installed about 6 for one extended family. The sets had been sized and bought and were onsite.
They were all too small.
All of the owners had a lot of air conditioners.
The sets could not pick up the load.
At first it was trial and error. Turn off all the A/C and restart one at a time.
six sets and a couple of dozen A/Cs later I had a very accurate idea as to how big a motor a standby set could and could not start.
Then came the work-arounds.
My basic solution was an extension cord, a 6" x 6" x 4" junction box a normally open push button and a two or three pole power relay.
One for each A/C.
When you pushed the button the relay pulled in and sealed itself in.
When the power failed all the relays dropped out and all the A/Cs stopped.
The A/Cs had to be restarted individually.
Each customer knew how many A/Cs he could run without stalling the genset.
Within about five years I had replaced all of the small sets with larger sets that I had sized properly.
CuriousElectron said:
Has anyone had a chance to witness an undersized generator unable to bring connected motor up to speed?
Yes. Many times.
Bill
--------------------