Aug 8, 2007 #1 mokwadi Electrical Joined Jul 27, 2007 Messages 3 Location A1 How are current transformers and the relay connected for a standby earth fault protection scheme?
Aug 22, 2007 #21 RalphChristie Electrical Joined Jun 25, 2002 Messages 648 Location ZA I haven't seen standby schemes on solidly grounded transformers before, thanks for the correction. Lesson learned! Raghun: RalphChristie said: Remember, on a delta/star transformer, an earth-fault current on the secondary side is seen as a phase-phase fault on the primary side. Click to expand... Thanks Regards Ralph [red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red] Make the best use of Eng-Tips.com Read the Site Policies at FAQ731-376 Upvote 0 Downvote
I haven't seen standby schemes on solidly grounded transformers before, thanks for the correction. Lesson learned! Raghun: RalphChristie said: Remember, on a delta/star transformer, an earth-fault current on the secondary side is seen as a phase-phase fault on the primary side. Click to expand... Thanks Regards Ralph [red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red] Make the best use of Eng-Tips.com Read the Site Policies at FAQ731-376