mmt019
Electrical
- Jun 25, 2003
- 63
I have a 15kV class switchgear rated 1200A 3-phase, 3-wire system, delta. THe utilization voltage will be changed from 6.9kV to 12.47kV. What PT ratio should be used? I will be using 2 PTs in an open delta configuration. Standard ratios that are available are 14,400/120V (120:1) and 12,000/120V (100:1). Most PTs are designed for 10% over nomimal utilization voltage, continuous rating. The PT ratio that was used at 6.9kV was 7200/120V (60:1). I do not think there are any disadvantages if I use 14,400/120V PTs. For example, on a 480/277V wye system, the standard PT ratio is 288/120V with nominal L-N voltage of 277V. In essence, do you goto the next higher PT primary voltage if your utlization voltage is between available primary PT voltages?