I have a client that is asking me to use a detail from another firm. The connection is on a non-composite insulated precast wall with integral continuous corbel to support hollow core plank. They have placed both the as corbel reinforcement and the out-of-plane wall anchorage reinforcement with the tail of the hook in direct contact with the foam insulation. I assume that the thinking is that no cover (environmental) is required because the concrete is in a dry condition within the composite wall.
Ingnoring the merit of that argument, will the hooked bar be developed (assuming that full ldh is provided) if there is no concrete on the outer edge of the hook tail?
It seems to me that the tail still needs to develop tension. When the tail starts to load in tension as the load tried to pull it around the bend, it will deform up into the foam and have no anchorage in the tail. If the bend was sufficient without the tail being anchored, we would not need any length to the tail beyond the bend.
If you cast a sample with a bar tight to the form (0 cover) and test it for tension I don’t think it would take much load before spalling out the face. In Section 12.2.3 EQ 12-1, ld would result in a division by 0 error due to cb and Ktr both being 0. As cb approaches the limit, ld is going to infinity so no development length would satisfy. In the commentary on Section 12.2.2 it states “With less cover and in the absence of minimum ties or stirrups, the minimum clear spacing limits of 7.6.1 and the minimum concrete cover requirements of 7.7 result in minimum values of cb equal to db. Thus, for “other cases,” the values are based on using (cb + Ktr)/db = 1.0 in Eq. (12-1).”
This tells me that 12.2.2 other cases is not applicable for cb Less than db.
Ingnoring the merit of that argument, will the hooked bar be developed (assuming that full ldh is provided) if there is no concrete on the outer edge of the hook tail?
It seems to me that the tail still needs to develop tension. When the tail starts to load in tension as the load tried to pull it around the bend, it will deform up into the foam and have no anchorage in the tail. If the bend was sufficient without the tail being anchored, we would not need any length to the tail beyond the bend.
If you cast a sample with a bar tight to the form (0 cover) and test it for tension I don’t think it would take much load before spalling out the face. In Section 12.2.3 EQ 12-1, ld would result in a division by 0 error due to cb and Ktr both being 0. As cb approaches the limit, ld is going to infinity so no development length would satisfy. In the commentary on Section 12.2.2 it states “With less cover and in the absence of minimum ties or stirrups, the minimum clear spacing limits of 7.6.1 and the minimum concrete cover requirements of 7.7 result in minimum values of cb equal to db. Thus, for “other cases,” the values are based on using (cb + Ktr)/db = 1.0 in Eq. (12-1).”
This tells me that 12.2.2 other cases is not applicable for cb Less than db.