I cannot imagine what they could possibly think to acomplish by using current limit continuously on a crusher. In starting, yes, but in running, no benefit whatsoever. I think that you may be confusing the two conditions. It is very common to use current limit starting on portable equipment because they are often supplied from portable generators, and the limited power source can be best accommodated with current limited starting. Having it current limit after it is at full speed would do nothing useful, and more likely would harm the motor or stall it at least.
Where the confusion may come from is that some soft starters are made very cheaply, and are Voltage Ramp only, or can only current limit for a very short time before they must go into bypass or at least full-on so that the SCRs do not overheat. Other heavy duty soft starters will allow the current limit function to override all other settings and stay in current imit until the motor accelerates or trips on overload. That may be what your ProSoft starter was doing, and that would be a valid issue. I do not know if the ATS-48 has the necesary capacity, but here in the US they are not used much on crushers and the like. They yend to get the pump and fan market.
"Venditori de oleum-vipera non vigere excordis populi"