Sprinklers in stairs
Ehendrix
63
Just digging into protection of stairs, when NFPA 13 2013 edition calls out protection under the first "accessible" landing, is this underneath the 2nd floor landing as you look up?
Thank you,
Eric Hendrix, SET
NICET Certified
Design Manager
I believe it is in reference to the first intermediate landing (i.e, where stuff could potentially be stored under).
13-13 8.15.3.2.3.1 seems to confirm this, by saying that if the space under the stairs is blocked off so that storage can't occur then you don't need any sprinklers at the bottom.
That is exactly what I thought and have thought for years as it goes directly into protection under the stair.
I guess the older I get I tend to rethink many positions, as a challenge to myself I suppose.
Eric Hendrix, SET
NICET Certified
Design Manager
There are many who still think it is above the door for egress. That is incorrect. To clarify, the required sprinkler will be around 5'-0" AFF depending on construction type.
R/
Matt
Just an aside, be aware of the difference between a stair and a stairwell.
We recently had an AHJ ask us to install sprinklers beneath every landing in a stairwell. NFPA 13 has a distinction between stairs and stairwells. Thankfully it was clearly worded enough to distinguish.
Good point. Most "Stairs" like Grand Stairs in a lobby, are actually Obstructions > 48". Sprinklers must then be installed throughout the area..
R/
Matt