Sprinkler lines being cored in wood ceiling joist?

Status
Not open for further replies.

rbhall

Civil/Environmental
Joined
Nov 24, 2011
Messages
21
Location
US
The contractor is installing his 1 1/2" branchline through a core in wood ceiling joist. The cores are approx. 2", does this allow for the proper movement in seismic catagory C. Is there any bracing required since the movement is fairly restricted? I am use to seeing pipe supported from threaded rods and never seen it installed thru wood members. The cores are properly placed to meet the IBC requirements.
 
Never mind the seismic problem. Does the structural engineer know of this? With 1-1/2" pipe, od=1.9" That leaves just 0.1" of joist. Not much strength left, unless there is more to it than stated.
 
Through a 2x10, 2X12 etc... plenty structural integrity left if cored through the midpoint of the joist..
 