Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sprinkler Head Clearances

Status
Not open for further replies.

robertst

Computer
Joined
Jun 5, 2006
Messages
1
Location
US
We are installing new cable trays in one of our older computer rooms that has a pre-action sprinkler system and a very limited ceiling height. I realize the clearance under a sprinkler head is 18", but is there a regulation that limits the tray distance from the ceiling if not directly under the sprinkler head? The cable tray that is being installed is a basket weave, open style tray. One tray will house network cables (fiber/copper) and the other is for power.
 
Check into NFPA-13 2002 edition starting a 8.6.5.2, this use to be called the beam blocking rule but has grown much over the last several editions of NFPA.

Hope this helps.

G3
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top