Sports Netting
Polecat
132
Does anyone have a source for determining the wind load on golf and baseball nettings? Are there some predetermined force coefficients to use or does one go into the solidity ratio method for partially open surfaces as per ASCE7?
Thanks for the reference, Wiktor. I checked the thread and it seems that I'm not the only one who has been confronted with this question. And, it also appears that none of them have a real solution either! B-(
I have calc'd wind loads on a baseball field net.
I used ASCE 7-05, Figures 6-20 and 6-22 and compared the results between the 2 figures. Read the Figure Notes for how these tables can be used.
I requested the net info from Manufacturer (rope thickness and spacing) and calc'd the surface area per square foot of net and determined the pressure. A net is open enough that it doesn't meet the 30% requirement to be considered a solid sign (but I checked it anyway using the (1-(1-e)^1.5) reduction factor to see what it would do.
Hope this helps.
What happens when the netting catches trash, loose debris, leaves, etc.? What percent is open?