Splitting up wiring to smaller guages

Status
Not open for further replies.

hrc

Electrical
Nov 8, 2001
104
Feeding into a control box with a 208Y feed, using 6/5 SO cable, full load on the system is 43.846A/phase

[derived from having a power supply with a draw of 14.42A, so using two legs and three supplies split across, each phase will see a draw of 28.8A, and then a 15A single phase 120V load for each phase]

So, the main feed from the load side of the control box breaker will come to a terminal block using #10 wire (free air), and the other side feeds two power supplies AND the 115V outlet. So the PS see a draw of 28.8A and that requires #14. Tapping off this phase and the neutral, the 15A feed only needs #18. So is it 'legal' to take two different wire sizes off the terminal block, or the studs of the circuit breaker?
 
Replies continue below

Recommended for you

Not in general. The wire must be protected by the upstream overcurrent protective device. #18 would not be protected by a 15A breaker.

There are "tap rule" exceptions in the NEC that might allow this under certain situation, but I don't think #18 could ever be used.

 
Per my charts, in free air, copper wiring #18 is good to 16A
 
I just happened to have a copy lying around of the now cancelled MIL-C-5809/1 spec which used to qualify circuit breakers.

The first important condition to be noted is that these standard circuit breakers have an ultimate trip limit of 138%, which means that for some short period of time a 15A circuit breaker could allow up to 20.7A (15A X 1.38 = 20.7A) to flow through your wire.

The second condition (and most important to your application) is that these standard breakers have a lower trip limit of 115%, which means that the circuit breaker could allow 17.25A (15A X 1.15 = 17.25A) INDEFINITELY.

The circuit breakers you are contemplating may be qualified to a different spec, but the same principle applies when sizing a circuit breaker to protect wire. You have to know as a minimum (there are other factors) what trip limits your circuit breaker will have so that you can characterize accurately what your wire will experience.

Best regards,

Debodine
 
Thanks for that insight, should have been obvious to me on that one.
 
If this is an installation covered by the National Electrical Code, the smallest conductor allowed for 15A branch circuits is #14. Also, whatever termination devices or lugs you are using would also have to be UL listed for #18 wire.

Molded case circuit breakers rely on the connected conductors as a heat sink to keep the breaker from overheating and tripping below its rating. UL testing for 15A (and smaller) breakers is done with #14 AWG. So, that is smallest size conductor that can be (legally) used for NEC compliance.

 
I was planning on using #14, thanks for the confirmation. This is a power chassis, and will be run the NRTL certifcation so yes, it will be a NEC covered product.
 