What do you mean by split range?
To me split range means a 4-20mA output runs to two valves, each of which is ranged differently, for instance, one valve opens continuously over the 4-20 range, the other valve starts to open at 12mA and opens fully at 20mA.
Any controller with a 4-20mA output can do that, because the ranging is set up on the valves positioner.
If by split range, you mean two outputs that operate on either side of the setpoint,for example, one output for heating (operates below setpoint), one output for cooling (operates above setpoint), then your choice is far more limited.
For duplex operation like heat/cool, I tend to use Honeywell UDC 1/4 DIN controllers 2500, 3200), because the setup is straightforward and it doesn't use numerical codes, it uses descriptive terms. The new P.I.E. software is great help for keeping track of different setups on different controllers.
Dan