7.9 Tank access
Fo safety reasons a tank have to means of egress from the roof. For a single tank, which is not interconnected with another, then the second means of access is usuallu by a vertical-caged ladder.
The BS 2654, API 650 and prEN 14015-1 Codes all specify similar design requirements for access ways but in using these the designder must also be aware of any local and/or client requirements ans safety issues.
Whilst there are some differences between the tank Codes, the principal requirements are as folows:
*Min clear width of a staircase, platform or walkway shall be 600 mm.
*Min height to the top handrail of a horizontal platform or walkway shall be 1070 mm.
*Min depth of a stair tread shall be 200 mm.
*Max slope for a staircase 45° (50° in API)
*Handraling is required on the inside stringer of a spiral staircase where the gap between the stringer and the tank shell exceeds 200 mm.
*The normal "going" and "rise" for treads of a spiral staircase is 200 mm.
*The max vertical rise between intermediate platforms of a staircase is 6 m.
*Vertical ladders over 4m high shall be fitted with safety cages. BS 4211 allows a max height between intermediate platforms of 9m but it is normal to limit this to 6m on tanks.
7.9.1 Spiral staircase
Probably the most common means of access is the spiral staircase. This type os staircase is simple to fabricate and erect. ...
There are long-term disadvantages with this type of staircase, and these are:
*Being welded directly to the shell makes corroded treads difficult to replace (galvanized treads cannot be used because of the health risk in welding on to a galvanized surface).
*Where tank shells are thermally insulated, there are numerous penetrations in the cladding where the dogleg supports and trads pass through and offer a path for the rain to get in and cause corrosion on the shell.
*The tread replacement issue can be solved by using bolt on treads where a short lenght of drilled angle is welded toe on the shell to which the tread is bolted. Similarly at the outer tread support a short length of drilled flat is welded to the support to carry the tread.
*Because of the shortcommings of the weld on staircase, most spiral staircase today are constructed with an inner and outer stringer and bolted galvanized treads. The stringers are supported off brackets welded to the shell but the limitations in the Codes regarding the welding of permanent attachments to shell musr be observed.
*The double stringer spiral staricase is to be preferred for thermally insulated tanks because of the smaller number of penetrations in the cladding.
7.9.2 Radial staircase
This type of staircase is often used to access large diameter tanks, which have large bunded areas. ...
7.9.4 Vertical ladders
Tank operators do not favor vertical ladders as a main means of access to a tank roof because they are tiring to climb and require the full use of all limbs during the ascent, hence the carrying of any sundry equipment is difficult. However as a secondary means of escape from a tank roof under emergency conditions when the primary route is blocked or otherwise unavailable, then they are most welcome. ...