specs for foundation on fat clay

Status
Not open for further replies.

gte652p

Electrical
Joined
Jan 19, 2009
Messages
3
Location
US
I am looking for any DOT spec in Tennessee for a foundation on fat clay...on a previous job in Mississippi the DOT spec called for No. 610 crushed limestone compacted.

Is there anything in TN like this? Or could I be pointed to a ASTM spec?

Note: I am not a civil engineer, I am electrical but trying to research this for someone else.

Thanks.
 
I also should have also added this is for a substation transformer pad.
 
The better way is to consult a geotech who knows the local.
 
google TNDOT base specifications........



I second the geo-consult.....fat clay is many things to many people. If I had fat clay where a foundation (slab) was planned...I would either treat with lime and or undercut then replace with suitable material...then proceed with base material ...if necessary.
 