DOES ANYONES HAVE A CLUE WHERE I COULD LOCATE A SAMPLE SPECIFICATION FOR A CURRENT LIMIINT REACTOR/SERIES REACTOR.
 
Last edited:
The "specification" is usually what the end user requires in terms of performance: how much current to carry, how much loss (iron and copper) is acceptable, applied voltage, method of protection, overall power quality, cycle of use (which may be continuous, but may not), environment of application, etc.

Note that above a certain rating, almost all (high power) reactors are custom products ... or at least semi-custom. That means the manufacture is done with present raw material prices - which are going to be higher than in recent years as the components of a reactor tend to be copper, steel, and insulating media.

Also - just because the cost seems to be a "fortune" to the OP does not mean it's a fortune to others. Quantitative description is (almost) always better than qualitative.
 
The "specification" is usually what the end user requires in terms of performance: how much current to carry, how much loss (iron and copper) is acceptable, applied voltage, method of protection, overall power quality, cycle of use (which may be continuous, but may not), environment of application, etc.

Note that above a certain rating, almost all (high power) reactors are custom products ... or at least semi-custom. That means the manufacture is done with present raw material prices - which are going to be higher than in recent years as the components of a reactor tend to be copper, steel, and insulating media.

Also - just because the cost seems to be a "fortune" to the OP does not mean it's a fortune to others. Quantitative description is (almost) always better than qualitative.
I probably should have worded my question a little differently, but I am more specifically looking for a sample specification for purchasing a reactor.
 
I'd contact Trench. They should be able to help you out.
 
Although reactors are custom made, it is fairly straight forward to specific them by looking through the applicable IEEE standard and filling in the blanks. Here are the technical portions from a fairly old specification. I second the advice to talk with Trench, as they have been helpful to me in the past.

Be aware that reactors cause large magnetic fields that can damage nearby rebar or steel support structures. Design of the foundation and supports can harder than purchasing the reactors themselves.

5.08 REACTORS
5.08.1 NAMEPLATE REQUIREMENTS
The nameplate shall be stainless steel or anodized aluminum permanently imprinted, scribed and/or embossed with all the information recommended per IEEE Std. C57.16-1996, Section 12.1.1
5.08.2 MOUNTING REQUIREMNTS
5.08.2A PHASE SPACING
The reactors will be mounted 12 feet on center.
5.08.2B PEDESTUL
The reactors shall be capable of being mounted on the existing pedestals shown in drawing xxxxxx. If the existing pedestal is not satisfactory, pedestals must be included.
5.08.3 FACTORY TESTING
All routine tests shall be performed in accordance with ANSI/IEEE Std. C57.16. In addition, the following tests should be performed:
Switching impulse test
Chopped–Wave impulse test
Audible sound test
5.08.4 INSULATOR MATERIAL
Insulators shall be wet process porcelain, glazed, light gray (Munsell 5BG 7.0/0.4, ANSI 70).

5.01.3 Current Limiting Reactor​

Current limiting reactor with the following characteristics.


Required Performance Rating
Value
Voltage Class
115 kV​
BIL Rating across coil
550 kV​
BIL Rating across insulators
550 kV​
Continuous Current
700 Amps​
Frequency
60 Hz​
Inductance
5000 µH
Mechanical short circuit withstand
53 kA​
Thermal withstand time
3 seconds​
Thermal withstand current
18 kA​
Seismic Level
Zone 3​
Atmospheric conditions
Industrial​
Phase centerline spacing
12 feet​
 