A most interesting topic.
I would guess 25% of my projects dealt with special sprinklers but if you include residential sprinklers I would boost that figure to 50% or better. If you want to include special sprinklers for storage then boost the figure to 75% or better.
As far as inspections the sufficiency of design shouldn't be dealt with less the inspecting company get themselves into legal troubles.
Let me explain that one. Say an inspector pokes above a suspended ceiling, notices a combustible space withoutt sprinklers and writes it up in his report. The owner gets the report, authorizes sprinklers be added to the space, the inspectors company gets a purchase order for the work and everyone is happy.
The danger lies in the scope of work involved in an inspection. An inspection is a visual walk through, ringing the bells and performing a main drain test. That is it, nothing in NFPA #25 directs an inspector to get on a ladder to poke his head above a ceiling and if he does so he is taking on a burden that shouldn't be his. By finding one non-sprinkled area, he got on a ladder to poke his head above a ceiling, it could be implied this was within the scope of his job and it would be reasonable to assume he poked his head up above all the ceilings checking for non-sprinkled areas.
If there is a fire in a different area of the building and let's assume it starts in an area above a suspended ceiling with combustible construction. If the loss is big enough look out for lawyers because the inspector implied on a previous report he checked above suspended ceilings as part of the contract.
I know, sounds foolish but we are talking about lots of money and lawyers.
Don't allow your inspectors to pass judgement on the sufficiency of a system. They should know NFPA #25 inside and out and their inspection should cover exactly what is contained in NFPA #25. Nothing more, nothing less. Make sure your inspectors know it and follow it exactly.
Suffiency of design. The inspector doesn't know the history of the building. Some time ago I did a job per NFPA #13R using dry pendent sprinklers which you are allowed to do as long as the dry pendent sprinklers are quick response and no more then four sprinklers are within a dwelling unit.
This is known as the "Motel Rule".
Problem I had is I needed to use five sprinklers; there was a mechanical closet that was normally locked but located within the dwellign unit. I submitted drawings with five sprinklers writing a letter to the local authority having jurisdiction advising him to reject the plans. I went so far as to tell him what to write so I could appeal tot he Board of Standards and Appeals comprised of members appointed by the governor having the legal authority, by statute passed by the state legislature, to waive anything they wanted.
The board was comprised of five members; a lawyer, a school teacher, a registered architect and two professional engineers. Knowing one of the engineers I was fairly certain I would receive a legal waiver but I had to make sure to do everything I had to do to cover my rear end.
If an inspector examines the system for compliance, and he shouldn't because that is not in the scope of NFPA #25, he is going to list a design descrepancy that doesn't exist.
I always urge designers to take care not to blindside an examiner or inspector. In many areas of the country those charged with reviewing sprinkler plans and inspecting the installation can not possibly know everything you know. If you run into something like I did be foreward about it, don't try to talk "him" into approving something he should not without at least providing something he should hang his hat on. What you might want to think about, in terms of an acceptable alternate, is contact a PFE like stookey, explain the situation, see if he will write a letter for a small fee (maybe a couple hundred bucks) so everyone involved, including the local fire chief, has some cover should something happen.
"The 2007 edition of NFPA 13 has made a darn good attempt of getting the information about the system posted at the riser. See NFPA 13 Section 24.6." Very much needed and long overdue.